I've got a friend who wants to install a subpanel in a laundry room. It's been a while since I looked at an NEC so I was wondering what are today's clearance restrictions between a panel/subpanel and a water source such as a sink/tub/washing machine. I seem to remember a 6' clearance being mandatory, but that was a while ago.
Peace |
Member Since
04/09/2008
Total Contributions
30 Posts
|
| Post Reply | Watch this Topic |
no rules |
04/21/2008 09:33 AM |
househelper |
There is no rule in the NEC about proximity to a sink or washer. You do need to have a clear space 30" wide and 36" deep for the panel to reside in. It does not have to be centered in that 30" space. |
Member Since
04/01/2005
Total Contributions
235 Posts
|
| Post Reply | Watch this Topic |
am I tripping? |
04/21/2008 12:04 PM |
sailor86 |
Then it must be an old rule or a local one because I could almost swear there was such a rule some time back. (I haven't roped houses in 10 years.)
Peace |
Member Since
04/09/2008
Total Contributions
30 Posts
|
| Post Reply | Watch this Topic |
Applies to bathrooms |
04/21/2008 02:56 PM |
TimBonham |
There IS a code rule prohibiting panels/subpanels inside a bathroom. That may be what you are remembering.
Your local inspector will decide whether a laundry room is similar enough for that rule to apply. Some inspectors can be quite stringent, even arbitrary. |
Member Since
01/10/2007
Total Contributions
117 Posts
|
| Post Reply | Watch this Topic |
I checked....you're right |
04/22/2008 09:32 AM |
sailor86 |
I contacted my local code enforcement office and like you said, no panels in the bathroom but beyond that, only working clearances apply.
Peace |