Adding a 240v into room. |
10/19/2009 07:16 PM |
bobbypassout |
Im confused with the formula-
Watts / volts = amps
Im running a wire from my one room to fuse box. Its going to be #10/2 wire on a 30 amp breaker. The equipment can be powered by 120v or 240v by simply changing the powercord, which has 3 prongs for the 240v. My equipment is 3000 watts and im almost possitive its 33 amps total. The equipment will run for about 8 hrs a day. My question is with the formula. Since im going with a 240v will it bring the total amps to 12.5 instead of the 33amps. 3000w/240v = 12.5amps. and then my 240v 30 amp breaker will be fine or do i have to go with 240v 8/2 gauge wire 40 amp breaker. thank you so much for your time and input. |
Member Since
10/19/2009
Total Contributions
3 Posts
|
| Post Reply | Watch this Topic |
What is the equipment? |
10/20/2009 11:54 AM |
househelper |
And you would have to do more than just change the power cord.
3000W/240V=12.5A is correct. If it will run for more than 3 hours, then you apply a 1.25 factor bringing the amperage to 15.6. This could be wired using 12ga and a 20A breaker. |
Member Since
04/01/2005
Total Contributions
265 Posts
|
| Post Reply | Watch this Topic |
distance from breaker panel |
10/20/2009 01:33 PM |
LarryG |
doesn't that make a difference also? |
Member Since
07/23/2004
Total Contributions
939 Posts
|
| Post Reply | Watch this Topic |
Wiring room 240v to handle 3000 watts |
10/21/2009 07:39 AM |
bobbypassout |
Thanks for the quick response. The distance from the room to fuse box is approx 50 ft of wire. I bought 10/2 gauge wire and a double 30amp breaker. The equipment is 3 1000 watt Quantum ballast(H.I.D Lighting). The equipment if im not mistaken will run for 8hrs a day. And with these ballasts there is a optional cord for 120v and 240v im going with the 240v both plugs are included for either 120v or 240v. Im still getting told that i have to run 10/2 and others are saying 10/3. I just want to make sure i install the right gauge wire so my electrician can just hook it up at box. I will return the breaker and 10/2 wire if need be. |
Member Since
10/19/2009
Total Contributions
3 Posts
|
| Post Reply | Watch this Topic |
Straight 240? |
10/21/2009 10:29 AM |
househelper |
If these are straight 240V lights (and they should be) you need 10/2 with ground not 10/3.
I'm almost afraid to ask what you might be doing with that kind of lighting in a residential setting.
Of course, if it is not residential, then you should not be doing any wiring there unless you are licensed, and if you were, you wouldn't be here. |
Member Since
04/01/2005
Total Contributions
265 Posts
|
| Post Reply | Watch this Topic |
type of equipment |
10/22/2009 07:16 AM |
bobbypassout |
im just gonna go on the safe side and go with 8/2 with ground black wire white wire and bare ground on 40 amp breaker 240v. thanks for all your responses and hopefully this keeps my wife busy for a few hrs a day. |