Adding receptacles to existing 20amp dedicated line.

02/07/2008 08:52 AM Drewska

Heres the deal. I have a 20amp dedicated line (10 gauge)that runs a 1200 BTU air conditioner in my living room. The AC unit draws 8.3 amps. It is used infrequently maybe three weeks out of the whole year. I want to tie in to the receptacle ans add two new receptacles and two new over head lites with switches. These are all low load. drwaing a total of maybe 3 amps. CAN I DO THIS? EVERYTHING I'VE READ SAYS I NEED A DEDICATED CIRCUIT FOR THE AC UNIT. IF MY UNIT DRAWS 8.3 AMPS AND THE EXTRAS I WANT TO ADD WILL DRAW 3 AMPS THATS A TOTAL OF 11.3. ON PAPER IT SEEMS LIKE IT WOULD NOT OVERLOAD THE CIRCUIT. Also the current receptacle has 10/2 gauge running to it. I have a spool of 14/2 I want to use. Can I do that or do I need to run 10/2 ???

Member Since
02/07/2008

Total Contributions
12 Posts

Post Reply | Watch this Topic
Indent

Circuit

02/07/2008 06:58 PM Tom O
Indent

Adding receptacles to existing 20amp dedicated line.

02/08/2008 01:18 PM Drewska
Indent

Dedicated Circuits

02/08/2008 03:29 PM Billhart Moderator
Indent

Adding receptacles to existing 20amp dedicated line.

02/08/2008 04:01 PM Drewska






 