The 115 (primary) side of the transformer will be connected via spade terminals to the HUM on my funace fan board (since the furnace panel schematic shows those terminals as being on the 115 side) *** The transformer in the humidifier can not be disconnected from the board, so I would say not to use the 115V HUM terminals unless a handy box with a receptacle is wired from them so you can plug in the humidifier 115-volt cord. Then the 50 relay is unnecessary. and the 24V side will run to those two wires shown at the top left corner of the Aprilaire manual (24V terminals on the humidistat), *** leave them off - It is unusual for a manufacturer to put a transformer in the device that has no function. It is probably there to provide 24 volts for the circuit and the lower right side tells you NOT to use an outside 24-volt source; so the upper left 24-volt wires are probably for the 400 series. These All-For-Every wiring diagrams are dangerous. then I will wire the 2 wires from the solenoid valve DIRECTLY to the AA terminals on the humidistat and run the outdoor temp sensor and plug in the 115 gounded plug for the fan. *** The plug should power the fan and the internal circuit board through its internal transformer. By using the fan board for a 24V source, I am also gaining a current sensing relay (Instead of using the "Model 50")...right? Whew! Does that sound correct? *** The instructions say you don't need the 50 relay if the furnace controls the power to the humidifier, so that is correct. But you shouldn't need to connect to the 24 volts of the furnace. The fan in the Aprilaire will only run when the furnace fan board tells the Humidistat via 24V connection, which in turn triggers the solenoid valve right? *** If you connect ehe 115-volt plug to the 115-volt HUM terminals. Why is there even a 24V transformer built into the Aprilaire?? *** I would go through this wiring arrangement carefully following each and every step and drawing every circuit using only the plugged 115-volt wire and the internal transformer first, to see if that will power the solenoid from the transformer next to it. Everything else is a switch that breaks the wired path from transformer to solenoid. Will the transformer in the humidifier control the fan relay, solenoid AND use the controls outside the humidifier so the 24-volt line at the upper left is NOT required? Unfortunately, there is no wiring diagram or instruction that explains that clearly - one instruction negates the other. Clues point to the use of the internal transformer for all 24-volt power without another one used (thus the wires at the upper left not used.) The 115-volt plug-in is there so the humidifier can work independently of the furnace if desired without the 50 relay OR only when the furnace fan is on, with the 50 relay in the circuit. This can help for the installation, but it shows the separate transformer of the 600 model used: http://www.sheridanhvac.com/Aprilaire%20600%20Installation.htm [This message has been edited by HKestenholz (edited December 18, 2002).] |