COLEMAN EVCON FURNACE |
10/19/2006 11:01 AM |
SAMBOE |
POLIT LIGHT WILL NOT LIGHT, THE BLOWER COMES ON. AND THE 4 FLASHES INDICATE LIMIT SWITCH OPEN. COULDN'T FIND A RESET BUTTON WHAT NEEDS TO BE DONE OR REPLACED. THANKS TAMMY |
Member Since
10/18/2006
Total Contributions
2 Posts
|
| Post Reply | Watch this Topic |
4 FLASH LIGHT |
02/06/2008 01:46 PM |
ALDENLUMBER |
I HAVE THE SAME PROBLEM, LET ME KNOW IF YOU GET A HELP REPLY |
Member Since
02/06/2008
Total Contributions
2 Posts
|
| Post Reply | Watch this Topic |
wow me too |
02/20/2009 06:15 AM |
barbi71 |
i have the same problem, was able to fix it first time but not now. yes 4 flashes limit switch open. no reset button |
Member Since
02/20/2009
Total Contributions
1 Posts
|
| Post Reply | Watch this Topic |
Thermal protection |
02/20/2009 09:49 AM |
tlmoss |
look at the thermal switches in the fan housing of your air handler. These look like little round disks. They can be hard to spot sometimes. If one of them is shorted open, the system will not work. You can order these on-line and they cost about $20.00. If you are mechanically inclined it beats the repair bill. |