I've reread all your old posts......you came here with Very little electrical knowledge....asked only a few questions....(got some good advice).....Now you have problems......
Dad used to eye-ball me and say
".....a LITTLE information is Dangerous....."
You need to educate yourself....read "wiring simplified"
START by telling us WHAT you actually ended-up-doing....nice and slow.....
You were planning on starting at the A/C circuit ?
Troubleshooting is an ART.........often difficult ONLINE......the more info you bring to the table the better......
Are you still using the DVM ?....do you have a cheap neon tester or LampSocket w/leads ?
You mention the furnace....is that 220 volt ?
"" I have to reset the main breaker.""
I don't understand....did the Main trip ?
Is there any Brightening of lights.....this is the "Missing-Nuetral" problem.........
It kinda sounds like loose connections......But why/what the problems with some 220 volt appliances....be specific.....
Did-ya-use the Push-in backstab connection receptacles......always a problem....Screws!
Are the wire-nuts tight ....sized correct.....fully seated.....
you had 14-2 NM-B and a 20 amp breaker "in stock"........what did you change ?
Your problems ALSO could stem from the POCO.....
What does the incoming service LOOK like.....DON'T TOUCH ANYTHING.....I'm just asking....
Is it new/nice in the city......Old Co-Op 1000' run thru the trees?
"...measure once.....cut twice....throw that one away and cut a new one...." |