Spa Wiring |
02/17/2008 10:21 AM |
viclibo |
I have a hot tub that has only connections for 2 hots and a ground. My 50 amp sub panel has a gfci breaker with the hard wired neutral connected to the neutral bus bar in the sub panel. The GFCI itself has places for 2 load hots and 1 load neutral. Since the hot tub has no neutral point of connection, can I ignore the neutral completely? |
Member Since
02/17/2008
Total Contributions
3 Posts
|
| Post Reply | Watch this Topic |
Yes |
02/18/2008 11:26 AM |
househelper |
As long as the white pigtail from the breaker is connected to the neutral bar in the subpanel, this will work with only the two hots connected to the breaker. |
Member Since
04/01/2005
Total Contributions
237 Posts
|
| Post Reply | Watch this Topic |
Thank You |
02/19/2008 08:42 AM |
viclibo |
Thank you for the response. I appreciate your time |