Temperature Pressure Relief Valve |
07/20/2008 03:12 PM |
tjw1961 |
Hi,
The Temperature Pressure Relief Valve on my 9 year old AO Smith water heater has started to drip. It only does this when we use our central air. Any ideas on why or what I should do about it? I am planning on replacing the valve tomorrow, but find it curious that it only leaks when the air is in. The water heater is about 4 feet from the furnace, which is what circulates the air. It's a forced hot air system. Any help will be appreciated.
Thanks,
tj |
Member Since
07/20/2008
Total Contributions
2 Posts
|
| Post Reply | Watch this Topic |
doesn't make sense. |
07/20/2008 04:21 PM |
LarryG |
it has to be condensation.and i'm going to be surprised if replacing the t+p valve cures the drip. |
Member Since
07/23/2004
Total Contributions
886 Posts
|
| Post Reply | Watch this Topic |
TPR Valve |
07/23/2008 12:46 PM |
tjw1961 |
Thanks, it turns out it was the water heater expansion tank. It had blown and wasn't regulating the pressure correctly. After replacing it, it turned out the Temperature Pressure Relief Valve wouldn't reseat and it was replaced also. Turns out the AC thing was just bad timing!
Thanks again,
tj |