light switches |
08/30/2009 03:32 PM |
cj9113 |
I have light switches that are not hooked to anything. when we turn them on they don't work. I don't know if it's hooked up the the breaker box. what i want to know if it's not hooked up to the breaker box can i hook it up to the outlet and make it work that way, by hooking a light to the outlet and make it work that way or is that a fire waiting to happen |
Member Since
01/14/2007
Total Contributions
14 Posts
|
| Post Reply | Watch this Topic |
useless switches |
08/30/2009 06:49 PM |
Tom O |
Frequently in residential work, switches can be used to control a receptacle. Usually, the tab that connects the top & bottom half off the receptacle (on the hot side) is broken off so that only 1/2 of the receptacle is switch controlled. If someone replaces the receptacle without breaking off the tab, then the entire receptacle is hot all the time & you end up with a mystery switch. |
Member Since
09/18/2002
Total Contributions
496 Posts
|
| Post Reply | Watch this Topic |
useless switches |
08/30/2009 09:03 PM |
cj9113 |
what do you mean by breaking off the tab. I bought the house and everything was new in the house so what do I have to do to see what you are talking about. I know thee is no power going to it cause I have tested it and nothing |
Member Since
01/14/2007
Total Contributions
14 Posts
|
| Post Reply | Watch this Topic |
useless |
08/31/2009 06:52 AM |
LarryG |
"I bought the house and everything was new in the house"
there you go.somebody "flipped"the house and goofed up the wiring. |
Member Since
07/23/2004
Total Contributions
935 Posts
|
| Post Reply | Watch this Topic |
what to do |
09/07/2009 10:10 AM |
cj9113 |
so what do i do to fix it. all the utlets work it's just the switches in two of the rooms. help please |
Member Since
01/14/2007
Total Contributions
14 Posts
|
| Post Reply | Watch this Topic |
we were just guessing |
09/07/2009 06:01 PM |
LarryG |
we were just guessing that someone replaced the recepticals and failed to note that the tab across the hots needed to be removed.
i see it happen all the time. |
Member Since
07/23/2004
Total Contributions
935 Posts
|
| Post Reply | Watch this Topic |
tabs |
09/13/2009 04:01 PM |
cj9113 |
what do you mean the tab across the hot needs to be removed?? |
Member Since
01/14/2007
Total Contributions
14 Posts
|
| Post Reply | Watch this Topic |
tabs |
09/14/2009 07:01 AM |
LarryG |
every duplex receptical has a snapoff tab across the hot screws that can be removed if you need to isolate one from the other for any reason. |
Member Since
07/23/2004
Total Contributions
935 Posts
|
| Post Reply | Watch this Topic |
 |
 |  |  |