need baseboard heating "fins" on bare pipe

01/16/2007 04:56 PM pingber

Here's an interesting question ...I have about 10 feet of baseboard pipe in my bedroom that doesn't have any fins on it. So basically, I don;t get heat from that section of pipe. Does anyone make any "clip-on" fins? or does anyone know how to "jury-rig" fins? I really don;t want to crack open the system and replace that length of pipe, especially in the winter.

Member Since
01/16/2007

Total Contributions
1 Posts

Post Reply | Watch this Topic

Fins

01/16/2007 09:47 PM HKestenholz Moderator

No, you'll have to install new fintube in place of the pipe.

www.heatpro.us energy businessmen's knowledge

Yes, you really have to find out the MAKE and MODEL to get good answers. There IS more than one machine made.

Member Since
05/02/2001

Total Contributions
4418 Posts

Post Reply | Watch this Topic

Have the same issue

01/27/2007 09:40 AM kharvey

I have Santa Fin system with only fins on 5 feet of a 20 foot run. Why was this done? Where can I find a snap on fin kit?

Member Since
01/27/2007

Total Contributions
2 Posts

Post Reply | Watch this Topic

Why is there only 5 feet of fin on 20 feet of pipe?

01/27/2007 01:26 PM HKestenholz Moderator

It was done because someone figured that you needed 5 feet of heat instead of 20 feet of heat. As each foot of baseboard gives about 600 btuh of heat when the water is at 180F in the coldest part of the year, the difference is 5 times 600 = 3000 btuh for the room, or 20 x 600 or 12,000 btuh for the room. As a newly built home needs about 25 btuh per sq foot -

5 ft of baseboard would be required in a room of 3000 divided by 25 = a 120 sq ft room or a
10 x 12 room

20 feet of baseboard would be for a 12,000 divided by 25 = 480 or a
14 x 20 room

putting 20 feet of baseboard in a 10 x 12 room would make it a sauna.

IOW - putting as much fin as can fit in an exposed length of pipe JUST BECAUSE YOU CAN isn't a good plan.

http://www.heatpro.us/designtree/documents/320102B9B4DD4BCB861A84E86CBA97E658AE380B.html

Planning ahead by having an accurate heat estimate for the room and installing the PROPER length of finned tubing to provide the required heat without freezing or overheating you makes more sense.

www.heatpro.us energy businessmen's knowledge

Yes, you really have to find out the MAKE and MODEL to get good answers. There IS more than one machine made.

Member Since
05/02/2001

Total Contributions
4418 Posts

Post Reply | Watch this Topic

But the room is an icebox right now.

01/29/2007 09:10 AM kharvey

It is a 12X12 room with a cathedral cieling and skylight. It also gets very liitle sun light. This room is on the second floor and is the first room on the run.
Seems like 20ft of fin is too much but 5 more feet may do the trick. Any idea if you can buy fins and attach them to the existing piping?

Member Since
01/27/2007

Total Contributions
2 Posts

Post Reply | Watch this Topic

Steps to heat

01/29/2007 09:16 AM HKestenholz Moderator

Do a heat estimate of the room and put in new finned tube to the length = the heat estimate for the room divided by 600. Then you'll have enough heat. There are NO clamp-on fins.

www.heatpro.us energy businessmen's knowledge

Yes, you really have to find out the MAKE and MODEL to get good answers. There IS more than one machine made.

Member Since
05/02/2001

Total Contributions
4418 Posts

Post Reply | Watch this Topic

Any luck finding the FINS

12/25/2008 10:06 AM medicinemaan

Hi i in the same situation. FINS are missing its cold and i need to replace the fins NOT the pipe. any help or suggestions are appreciated thanks

Member Since
12/25/2008

Total Contributions
1 Posts

Post Reply | Watch this Topic

Mystery situation

12/27/2008 09:30 AM HKestenholz Moderator

You don't know if the situation you are in is from not having enough water flow through the fins you have due to air bubbles or a clog, or closed valve, or if there really aren't enough fins. It is very rare that an installer won't put enough fin in the room based on a heat estimate need. It is more likely they will throw in the same lengths to buy.

As a check, do the heat estimate to know how many feet you need.

http://www.heatpro.us/designtree/documents/320102B9B4DD4BCB861A84E86CBA97E658AE380B.html

The other person above never got back with that info either.

www.heatpro.us energy businessmen's knowledge

Yes, you really have to find out the MAKE and MODEL to get good answers. There IS more than one machine made.

Member Since
05/02/2001

Total Contributions
4418 Posts

Post Reply | Watch this Topic
Page: [1]




About  | Press Room  | FAQ  | Contact  | Sitemap  | Privacy Policy  | Terms of Use  | Help

© 2009 BobVila.com