new furnace wont light

11/28/2007 10:11 PM cbittel

I bought a new Goodman furnace, installed it myself, it worked the first time I tried it, now it wont ignite. The led light is flashing.

Member Since
11/28/2007

Total Contributions
18 Posts

Post Reply | Watch this Topic

Guessman furnace

11/28/2007 10:52 PM HKestenholz Moderator

The light blinks in a certain way to tell you what the problem is. The code is on the lower inside panel and also in the instructions that come in the box with the furnace. It's always a good idea to read the instructions.

www.heatpro.us energy businessmen's knowledge

Yes, you really have to find out the MAKE and MODEL to get good answers. There IS more than one machine made.

Member Since
05/02/2001

Total Contributions
4065 Posts

Post Reply | Watch this Topic

new furnace wont ignite

11/29/2007 08:55 AM cbittel

Let me do this again. I have a goodman furnace that I installed yesterday, I did follow all directions and did everything I was supposed to do. The furnace did worked perfectly the first time I tried it, and now it wont ignite. The led light is flashing,I looked at the trouble shooting and checked everything It said to check, still no luck. The furnace is of course gas and it is a 69000 btu 95% efficent. Does anyone have any ideas?

Member Since
11/28/2007

Total Contributions
18 Posts

Post Reply | Watch this Topic

Regurgitation

11/29/2007 11:10 AM HKestenholz Moderator

Let me repeat it IN CAPS:

READ THE CODE NUMBER OF BLINKS
IT TELLS YOU THE PROBLEM TO SOLVE!

Reading is FUN da mental.

www.heatpro.us energy businessmen's knowledge

Yes, you really have to find out the MAKE and MODEL to get good answers. There IS more than one machine made.

Member Since
05/02/2001

Total Contributions
4065 Posts

Post Reply | Watch this Topic

new furnace wont ignite

11/29/2007 12:08 PM cbittel

PROBLEM SOLVED, KINK IN DRAIN HOSE WOULDNT ALLOW FURNACE TO DRAIN CORRECTLY. LED BLIKKS FAILD TO SHOW WATER BACK UP PROBLEM, IMAGINE THAT.

Member Since
11/28/2007

Total Contributions
18 Posts

Post Reply | Watch this Topic

Mr Ima gi na tion

11/29/2007 12:45 PM HKestenholz Moderator

But, it probably indicated a pressure venting problem. Imagine that. Still couldn't ace the people who would help you by asking for the blink code.

www.heatpro.us energy businessmen's knowledge

Yes, you really have to find out the MAKE and MODEL to get good answers. There IS more than one machine made.

Member Since
05/02/2001

Total Contributions
4065 Posts

Post Reply | Watch this Topic

new furnace wont light

11/29/2007 01:34 PM cbittel

your right, thanks for your help.

Member Since
11/28/2007

Total Contributions
18 Posts

Post Reply | Watch this Topic