no 'ground wires' present in wiring

03/15/2004 09:09 AM dan60510

Hi,
We're new homeowners, and are replacing our electrical switches & outlets, mostly for cosmetic reasons.

I noticed that the outlets I purchased have a green-screw that is intended for a ground-wire, however, none of the existing outlets being replaced are connected to such wires. I just don't a 'ground' wire present in our existing wiring. There's typically just two wires (the black & white).

Obviously I'm new to doing my own electrical. Is this wiring configuration typical for an 11-year old home? If so, how would the outlets be grounded?

Member Since
03/15/2004

Total Contributions
6 Posts

Post Reply | Watch this Topic

Grounded outlets

03/15/2004 10:42 AM k2

Hello Dan,

I'm not an electrician, but I'd be VERY surprised if an 11 year old home didn't have ground wires throughout.

Are you SURE there's no ground (bare) wire? If your junction boxes are metal, the bare wire might be attached to the BOX which would then ground through the receptacle's frame. I don't think this would be a great practice, but it's the only way I can see not having a visible ground wire.

If there ISN'T a ground wire, you MUST use 2-prong outlets--unless you replace with GFCI. Are the old receptacles 3-prong?



-k2 in CO

Member Since
06/07/2003

Total Contributions
1282 Posts

Post Reply | Watch this Topic

no 'ground wires' present in wiring

03/15/2004 11:15 AM dan60510

All of the existing outlets are three-prong, typically with just two wires, the black & white (hot & neutral).

Are you saying that maybe they configured the wiring so that the conduit & receptacle frames are serving as the ground?

-Dan.

Member Since
03/15/2004

Total Contributions
6 Posts

Post Reply | Watch this Topic

BX or sheathed electrical cable

03/15/2004 12:27 PM bcelect

What type of cable is used to feed the box? If it is armored cable (bx), then the ground is already there and should have a ground path. If it is sheathed electrical cable then the groung should be connected somewhere. In my house the guy who wired it connected the grounds on the outside, back of the box.It was inspected and passed back in 1959. Do you have either sheathed electrical cable or bx?

Member Since
02/22/2004

Total Contributions
139 Posts

Post Reply | Watch this Topic

sheathed electrical cable or BX

03/15/2004 12:36 PM dan60510

I have plastic-insulated wire running through conduit.

Member Since
03/15/2004

Total Contributions
6 Posts

Post Reply | Watch this Topic

all metal?

03/15/2004 12:43 PM bcelect

If everythng is metal ,then you should have an effective ground path, check by using a tester or a bulb from hot to metal. If it lights then you have a ground.

Member Since
02/22/2004

Total Contributions
139 Posts

Post Reply | Watch this Topic

ground

03/15/2004 12:46 PM bcelect

If you a gap between the metal box and the receptacle then you should use a self grounding receptacle or a ground jumper.You need metal to metal for an effective ground.

Member Since
02/22/2004

Total Contributions
139 Posts

Post Reply | Watch this Topic

metal receptacle

03/15/2004 12:49 PM dan60510

thanks. i was wondering if receptacles are designed so that they are grounded by the screws that attach the receptacle to the metal box.

that would be the only point of metal-to-metal contact that I can see.

Member Since
03/15/2004

Total Contributions
6 Posts

Post Reply | Watch this Topic

gap

03/15/2004 12:55 PM bcelect

if you have a space between the box and receptacle,,for the difference of drywall, plaster, tile and wood paneling. then by all means use a ground jumper. You are most welcome. Bruce

Member Since
02/22/2004

Total Contributions
139 Posts

Post Reply | Watch this Topic

no ground

03/15/2004 03:18 PM devildog

I'm not an electrician, but I do have a tester which tests for a ground. It is a plug that fits into a pocket and plugs into the outlets. It tells you if you have a ground, if the neutrals are reversed, or even if the outlet is working. I think it cost less than $10.

Did you have this house inspected? If yes, I would ask the inspector why he didn't catch this.

I think someone touched on the subject, but I THOUGHT it was against some regulation to put three pronged outlets in without having a ground. It's a little deceptive.

I think you need to test it and see if it is groundeand then go from there.

Good luck,
Devildog

Member Since
09/17/2002

Total Contributions
251 Posts

Post Reply | Watch this Topic