Home > Ask a Question > BBS > Insulation > roof ventilation

Insulation

Not Logged in.
Moderator Moderated by Handyman Login | Register
RSS
Page: [1]
Font Size:
   View Style: Flat    Tree
Post Reply | Post New Message
Title/Content Author

roof ventilation

11/24/2001 07:12 PM s armbruster

i have a question regarding ventilation in a cathedral ceiling. i recently changed the roof and rafters on an existing house from a 5/12 pitch to a 12/12 pitch roof. the rafters are 2x8 and i plan on using 6 in. r-19 fiberglass kraft backed insulation with the preformed dura vent foam panel to keep the air space open between the roof and insulation. i have installed a ridge vent and soffit vent. the question is, what should i do where the intersecting gable and valley rafters don't allow soffit ventilation through to the jack rafters? would the ridge vent be enough? this intersecting gable does face to the north and would be cooler than the rest of the roof. i thought about holes through the valley rafter but i would lose strength in the valley rafter. i assume that this would not be the best thing to do. if anyone has faced this this situation before please let me know what you did. thanks.

Member Since
11/24/2001

Total Contributions
1 Posts

Post Reply | Watch this Topic

roof ventilation

11/26/2001 12:15 AM DH

You need to ventlate the hips and valleys, the best way to do this is to drill a 2" hole as high as you can on the rafter, and then add an angled framing anchor.

Or glue and nail a 12" long piece of 1/2" plywood on the uphill side and then drill the hole thru.

Member Since
09/24/2001

Total Contributions
242 Posts

Post Reply | Watch this Topic
Page: [1]






 

About | FAQ | Contact | Sitemap | Privacy Policy | Terms of Use | Help
© BobVila.com 2008