Home > Ask a Question > Fix It Forum > Grounding Electrodes
Login | Register

Grounding Electrodes


Posted by Billhart Moderator on January 11th, 2009 01:23 AM
In reply to A few things. The power coming into your house is grounded by Bruno1949 on January 10th, 2009 09:43 PM [Go to top of thread]

Moderator Post (s) for this thread:
> Grounding generators and separately derived systems by Billhart on 01/11/2009
> Not True by homebild on 01/11/2009
> And By the Way by homebild on 01/11/2009
> Required grounding Electrodes by Billhart on 01/11/2009
> I Love it when the big boys go at it!!! by Jasper on 01/13/2009
> Portable or semi-portable generators by Billhart on 01/11/2009
> Ground wire by Billhart on 01/11/2009

"Hopefully a ground rod. Grounding to a water pipe is very out of date but still exists. "

If the water supply to the building is metalic and under ground and 10 ft or longer then it MUST BE USED AS A GROUND ELECTRODE.

However it can not be the only ground electrode.

In new construction, where applicable a UFER ground electrode is required. That is a conductor that is buried in the concrete footer.

If that is not available there are several other types of electrodes that can be used. But a ground rod is most common.

But a ground rod needs to be either tested for 25 ohms or less or TWO GROUND RODS ARE REQUIRED, 6 or more feet apart.

And if the water supply pipe is not metalic, but the internal piping is metalic then the water piping needs to be bonded to the ground electrode system.