COMMUNITY FORUM

SFM

08:53AM | 10/16/02
Member Since: 10/15/02
8 lifetime posts
Bvelectrical
I have a house that was built in the 50's which of course has no ground wiring. I have upgraded some of the outlets to GFCI outlets to provide some safety and so I can use 3 prong plugins. I am planning on upgrading my Fuse box to a modern Breaker box in the next few months. I have read that you can add a Circuit breaker GFCI to your breaker box. Does it make any sence to add a GFCI circuit breaker to the box if I already am protected with the GFCI outlets? Would it conflict with the outlets that are allready installed? Will it provide more safety?

Thanks,
SFM

Electrical Inspector

10:56AM | 10/16/02
Member Since: 09/27/02
73 lifetime posts
Hi SFM;
quote:

I have read that you can add a Circuit breaker GFCI to your breaker box.


yes, most panel manufacture's have GFI breakers available
quote:

Does it make any sence to add a GFCI circuit breaker to the box if I already am protected with the GFCI outlets?


It will then protect the circuit itself, which the plain GFI receptacles cannot do
quote:

Would it conflict with the outlets that are allready installed? Will it provide more safety?


It will not conflict, however , there is the possiblity of 'nusaince tripping' here.
For instance, if you were to have one of the newer gas ranges receptacle ( for the ignitor) served via GFI it would trip it.

There are also dimmers, as well as other electrical devices that may conflict with the 4-6 ma trip rating of a GFI.

Perhaps you should inquire of your local tradesmen about the new AFCI , and get thier take on your situation .


ACD

08:59AM | 10/17/02
Member Since: 10/15/02
359 lifetime posts
The main panel GFCI breakers are good if you are doing new wiring, or want to protect the entire circuit, the outlet units are if you just need to protect the bathroom outlet(s). If your bathroom is already protected, then you dont need to put in a GFCI for that circuit. If you plan to put in a whirlpool tub, then you will need a dedicated GFCI for that one outlet.

The other type of protection device isnt made to protect the bathroom, it is to protect the circuit from bad devices, or errant drill or saw blades. Say you have a light that has a damaged cord, the breaker will protect against that. National code now requires every bedroom circuit be protected by an Arc Fault device and all bathrooms and outlets near water, such as a kitchen or laundry area be protected by GFCI.

Here is what the 2 devices do; The AFI is a UL listed circuit breaker which is also classified for mitigating the effects of arcing faults. It protects from arcs between current carrying conductors above 75A (Square D AFI protects from arcs above 50A), and leakage to ground above 30mA.

The GFI is a UL listed circuit breaker which is classified for interrupting the circuit when more than 6mA of ground-fault leakage is detected.

In other words, the arc fault device wont protect against water hazards like the GFCI will, but the GFCI is too sensitve to protect against frayed light cords.

electricmanscott

04:20PM | 10/18/02
Member Since: 11/05/01
98 lifetime posts
Is this turning into an arc fault discussion? This 50's wiring what type is it? I am guessing some type of sheathed electrical cable with no ground as thats what I commonly see for that time. You would be better served perhaps to update some of the wiring after you get service done. Kitchen ciruits, bath receptacles, air conditioner receptacles, and such. I wouldn't spend the extra money on GFCI breakers for some of the reasons stated above. (Less control of what specific loads you are protecting)

[This message has been edited by electricmanscott (edited October 18, 2002).]

Electrical Inspector

01:04PM | 10/19/02
Member Since: 09/27/02
73 lifetime posts
point taken E-scott.

what would i tell a potential customer?

exactly what you allude to....

1)update the service

2)install new branch circuitry for those dedicated loads

3)lessen the lodas on any older circuitry, either via splitting up older circuits into 2-3 and/or derating those older 20A circuits to 15A

4)then, and only then, research options for said remaining older ciruitry.
One should not advocate AFCI's or GFCI's for the 'bandaid' approach......

SFM

05:05AM | 10/21/02
Member Since: 10/15/02
8 lifetime posts
Thanks for everyones help. I have decided to bring in a pro to install a new breaker box for me. I will install GFCI outlets where needed and AFCI breakers.
Click_to_reply_button
Inspiration_banner

INSPIRATION GALLERY



Post a reply as Anonymous

Photo must be in JPG, GIF or PNG format and less than 5MB.

Reply_choose_button

Anonymous

Post_new_button or Login_button
Register

Even though Halloween is past, pumpkins and gourds make great table decorations. That includes white pumpkins, too!  Here,... Filling an underutilized area beneath the stairs is a smart way to save space. Doing so with a stash of wood, however, is ... The Audubon Society inspired wallpaper in this Adirondack-styled entryway will get you in the outdoor mood. Grab your coat... Chalkboard paint opens up endless possibilities for customizing your dresser time and time again. Use chalk to label the c... A fireplace in the bathroom creates the ultimate setting for relaxation. Homeowners often choose electric or gas over wood... Yes, a freestanding garage can become its own tiny house. Artist Michelle de la Vega has all the comforts of a modern resi... There’s nothing like a new set of cabinet hardware to refresh a room. The possibilities are endless: Go modern, rustic, or... FLOR carpet tiles are a simple and affordable way to customize a floor covering for any space. You can make anything from ... Chalkboard paint features prominently in this elegant yet unpretentious headboard design. Add a new message daily to reflec... Salvaged boards in varying widths and colors make up the dramatic accent wall in this attic space. The high-gloss white of... The indecisive homeowner need not fret over choosing one (or even two) cabinet colors. The kitchen cabinets in this artist... Incorporate nature into your lighting scheme by securing a dead tree in a concrete mold and draping your pendant lamp from... Simple and striking, a couple of pieces of "lovingly used" furniture creates a special kind of charm. A weathered chair fo... First dress up your metal shelves with a coat of paint in an accent color that complements your kitchen decor. Then arrang... The vibrant green of Granny Smith apples make a beautifully natural alternative to the traditional evergreen wreath. Brigh...